Nulukkizdin
Structural
We've been asked to account for mechanical piping running through our composite metal deck on a project. Our initial intent was to have the pipes run below the slab, but it appears that this will be a major cost for the mechanicals that could be mitigated if they were able to go through the slab instead.
Details:
[ul]
[li]Composite steel beams[/li]
[li]2" VLI deck with 3.5" of concrete above the flutes[/li]
[li](2) 1" pipes will be passing through the deck in various places. We will encounter areas where the penetrations are perpendicular to the beam span and also areas where the penetrations are parallel to the beam span.[/li]
[li]Beam sizes are designed and fabricated. No options for up-sizing or redesigning beams at this point.[/li]
[/ul]
The most specific resource we have found as of now is ( You might need to open it with IE, for some reason Chrome/Firefox were having fits with it.
In this resource, the author mentions that pipes running parallel to the deck WILL have an effect on the concrete compression block considered for composite design. It appears that the article states that pipes running perpendicular to the deck WILL NOT have an effect on the concrete compression block. This seems a bit odd, as your compression profile (3.5" above the flutes in our case) would have a big chunk across it's whole width (1" in our case) taken out of it by the pipe.
The author does mention the effect on the shear studs as well. He mentions that pipes should be kept a minimum of 1.75 * (stud length) away from the stud centerline, or else that stud contribution should be ignored. Keeping these pipes as far away from the shear studs does make sense to me, but I'm not 100% sure about the conical shaped failure surface that he is discussing?
Additionally, we will have issues of both avoiding large moment conditions (makes sense to avoid passing a pipe over the midspan of a beam) as well as maximum shear flow conditions (at locations of max shear, we also have locations of max shear flow). "Losing" a stud at either of these max locations seems like it would be rather problematic for our design.
Soooo, after that long-winded introduction... Does anyone have any additional information on dealing with pipes running through a composite deck? Does anyone have any thoughts on how to quantify the effects of these pipes on the adjacent shear studs? Any idea on best practices (besides the obvious "don't put pipes in your slab")?
Any thoughts would be helpful!
Details:
[ul]
[li]Composite steel beams[/li]
[li]2" VLI deck with 3.5" of concrete above the flutes[/li]
[li](2) 1" pipes will be passing through the deck in various places. We will encounter areas where the penetrations are perpendicular to the beam span and also areas where the penetrations are parallel to the beam span.[/li]
[li]Beam sizes are designed and fabricated. No options for up-sizing or redesigning beams at this point.[/li]
[/ul]
The most specific resource we have found as of now is ( You might need to open it with IE, for some reason Chrome/Firefox were having fits with it.
In this resource, the author mentions that pipes running parallel to the deck WILL have an effect on the concrete compression block considered for composite design. It appears that the article states that pipes running perpendicular to the deck WILL NOT have an effect on the concrete compression block. This seems a bit odd, as your compression profile (3.5" above the flutes in our case) would have a big chunk across it's whole width (1" in our case) taken out of it by the pipe.
The author does mention the effect on the shear studs as well. He mentions that pipes should be kept a minimum of 1.75 * (stud length) away from the stud centerline, or else that stud contribution should be ignored. Keeping these pipes as far away from the shear studs does make sense to me, but I'm not 100% sure about the conical shaped failure surface that he is discussing?
Additionally, we will have issues of both avoiding large moment conditions (makes sense to avoid passing a pipe over the midspan of a beam) as well as maximum shear flow conditions (at locations of max shear, we also have locations of max shear flow). "Losing" a stud at either of these max locations seems like it would be rather problematic for our design.
Soooo, after that long-winded introduction... Does anyone have any additional information on dealing with pipes running through a composite deck? Does anyone have any thoughts on how to quantify the effects of these pipes on the adjacent shear studs? Any idea on best practices (besides the obvious "don't put pipes in your slab")?
Any thoughts would be helpful!