PagoMitch
Mechanical
- Sep 18, 2003
- 66
I have been designing hospital med gas and lab/commercial gases for decades. In few cases has the pressure rating of the gas piping (O2, N20, He, N2, Ar, etc) downstream of the tank(s) regulator been equal to or greater than the unregulated tank pressures.
For instance, for Medical Grade O2, a tank pressure of 2400 psig is regulated to 60-65 psig, transported thru the O2 piping for a designed 5 psi dp, and delivered to Patient Rooms outlets at 55-60 psig. Type L cleaned and capped 1" copper is rated at a nominal 420 psig. It has always been assumed that the pressure regulator does its job; and if it fails, the pressure relief valve does its job. I have never heard of a hospital or facility where both these systems failed simultaneously, discharging 2400 psi O2 into the hospital piping. If this were to happen, it would probably blow out the sealing rings on the O2 outlets, discharging 2400 psi O2 into Patient Rooms. If this had happened, everyone in the Healthcare world would have heard about it.
So.
We have a Lab project that requires delivery of mid to higher pressure gases to user provided equipment; 200 psig for Argon/Nitrogen, and 1200 psig O2.
The local branch of a "major national piping products" supplier has been tasked by the owner to provide the manifolds, regulator, PRV, etc. I am only providing the connecting piping.
In the process of doing their calcs, they have advised me that our selection of piping is inadequate, because the piping is not rated for the unregulated tank pressure.
For O2, tank pressure is 2400 psig, and our 1"/0.012" wall copper tubing is rated at 1500 psig - with a 4:1 safety factor.
For Argon and Nitrogen, tank pressures are 2000 psig, and our 3/4"/0.065" wall Type K copper tubing is rated at 724 psig - with a 4:1 safety factor.
In none of these systems is the piping rated to take unregulated tank pressure.
I have had multiple discussions with the company; our rep, and the factory engineers are adamant that our design is inadequate.
So either 1) there has been a major shift in gas systems design that I am unaware of (?), or 2) the players at the "major national piping products supplier" are in over their heads.
I sincerely hope it is not the former (although I will admit it is a possibility...), while it is difficult to believe it could be the latter. These guys have one job; piping systems. How could they get this so wrong?
I am reminded of a quote attributed to Charles Darwin - "Ignorance more frequently begets confidence than does knowledge".
TIA.
For instance, for Medical Grade O2, a tank pressure of 2400 psig is regulated to 60-65 psig, transported thru the O2 piping for a designed 5 psi dp, and delivered to Patient Rooms outlets at 55-60 psig. Type L cleaned and capped 1" copper is rated at a nominal 420 psig. It has always been assumed that the pressure regulator does its job; and if it fails, the pressure relief valve does its job. I have never heard of a hospital or facility where both these systems failed simultaneously, discharging 2400 psi O2 into the hospital piping. If this were to happen, it would probably blow out the sealing rings on the O2 outlets, discharging 2400 psi O2 into Patient Rooms. If this had happened, everyone in the Healthcare world would have heard about it.
So.
We have a Lab project that requires delivery of mid to higher pressure gases to user provided equipment; 200 psig for Argon/Nitrogen, and 1200 psig O2.
The local branch of a "major national piping products" supplier has been tasked by the owner to provide the manifolds, regulator, PRV, etc. I am only providing the connecting piping.
In the process of doing their calcs, they have advised me that our selection of piping is inadequate, because the piping is not rated for the unregulated tank pressure.
For O2, tank pressure is 2400 psig, and our 1"/0.012" wall copper tubing is rated at 1500 psig - with a 4:1 safety factor.
For Argon and Nitrogen, tank pressures are 2000 psig, and our 3/4"/0.065" wall Type K copper tubing is rated at 724 psig - with a 4:1 safety factor.
In none of these systems is the piping rated to take unregulated tank pressure.
I have had multiple discussions with the company; our rep, and the factory engineers are adamant that our design is inadequate.
So either 1) there has been a major shift in gas systems design that I am unaware of (?), or 2) the players at the "major national piping products supplier" are in over their heads.
I sincerely hope it is not the former (although I will admit it is a possibility...), while it is difficult to believe it could be the latter. These guys have one job; piping systems. How could they get this so wrong?
I am reminded of a quote attributed to Charles Darwin - "Ignorance more frequently begets confidence than does knowledge".
TIA.