Green white
Mechanical
- Jul 7, 2022
- 14
I have a pipeline with a DP of 900 psi that will be Hydrotested to 1125 psi
in this pipeline there are 6 ball valves to drain/ vent the pipeline. Those valves (rating # 600) and accordingly the max operating pressure for those valves are 1480 psi.
can I hydrotest the pipeline with valves in closed position, and without installing blind flanges because it is difficult to remove during the hydrotest?
in this pipeline there are 6 ball valves to drain/ vent the pipeline. Those valves (rating # 600) and accordingly the max operating pressure for those valves are 1480 psi.
can I hydrotest the pipeline with valves in closed position, and without installing blind flanges because it is difficult to remove during the hydrotest?