MTDENG
Structural
- Dec 12, 2009
- 2
We are pouring 8" thick, #5@15 EW, 14' tall walls with a 4000psi 3/4" mix. The pumper can't go below 4" hose for the 3/4" aggregate size and the design engineer wants to keep the 3/4" rock for strength and shrinkage. The 4.25" stinger the pumper has will not fit down inside the wall. A very informed shotcrete friend says he can design a 5000psi mix that he can pump through a 2-1/2" hose. I also considered building an oval steel chute 3"X12" that would attach to the boom pump's 4" hose. This would be placed inside the wall to within a few feet of the bottom. I always prefer to buy a tool if I can rather than make it, anyone seen anything like this? Or maybe just modify the mix and go with a 2-1/2" pump.
Tremieing into a wall with 3" or so clearance must have been done before thousands of times. Any help greatly appreciated.
On the one pour we did discharging from the top (dumb, dumb, dumb), the rebar did a fairly brilliant job of separating the coarse agg from the mix and depositing it on the bottom foot or so of the wall. Dumping a foot of gravel in the bottom of the forms before the pour would have achieved about the same result. Yes, we vibrated the wall well.
Thanks,
Michael
Tremieing into a wall with 3" or so clearance must have been done before thousands of times. Any help greatly appreciated.
On the one pour we did discharging from the top (dumb, dumb, dumb), the rebar did a fairly brilliant job of separating the coarse agg from the mix and depositing it on the bottom foot or so of the wall. Dumping a foot of gravel in the bottom of the forms before the pour would have achieved about the same result. Yes, we vibrated the wall well.
Thanks,
Michael