Good Day to all,
I need a plate heat exchanger to heat water to 60 C from 49 C. The hot fluid is propylene glycol, 60 % by mass conc, with Temp of 90C at in and 70 C at out.
Flow rates for both are fixed: 6 m3/h for water, 4 m3/hr for pgly
2 bidders came back with different proposals. Both use 0.6mm thick stainless steel plates. However bidder A has pressure drops across the HX in the order of 30-40 kPa for both hot and cold circuits, which is reasonable. The other bidder B has pressure drops in the order of 0.3kPa, which is soo low.
Bidder A claims that his overall HTC ( aka U) is around 3.6 kW/(m2C), while bidder B has a U of 0.75 kW/m2C.
As you can imagine, this allowed bidder A to use less plates, offering a smaller and lighter HX.
I was thinking that both datas make sense. Large pressure drops indicates bidder A uses smaller plate gaps, i.e. faster velocities, turbulent flow, better U. I concluded the difference has to be because of the plate gaps, but i am not certain. I do not have plate gap information, but i did request it...pending still.
I tried to do a preliminary verification of bidder A's design to estimate a range of U by modelling the flow as a rectangular duct with a very large aspect ratio, and using his dimensions. It didnt work. The answer i got was in the order of 0.5 kW/m2C.
Moreover, it is hard to believe that a vendor has a HX four times better than the other, especially when the liquids are the same and the plate material and thickness is the same.
Can anyone tell me a rough idea of the U value of this application. Where can I see past examples of HX's used so that I can believe bidder A. I want to believe bidder A!
Thanks
I need a plate heat exchanger to heat water to 60 C from 49 C. The hot fluid is propylene glycol, 60 % by mass conc, with Temp of 90C at in and 70 C at out.
Flow rates for both are fixed: 6 m3/h for water, 4 m3/hr for pgly
2 bidders came back with different proposals. Both use 0.6mm thick stainless steel plates. However bidder A has pressure drops across the HX in the order of 30-40 kPa for both hot and cold circuits, which is reasonable. The other bidder B has pressure drops in the order of 0.3kPa, which is soo low.
Bidder A claims that his overall HTC ( aka U) is around 3.6 kW/(m2C), while bidder B has a U of 0.75 kW/m2C.
As you can imagine, this allowed bidder A to use less plates, offering a smaller and lighter HX.
I was thinking that both datas make sense. Large pressure drops indicates bidder A uses smaller plate gaps, i.e. faster velocities, turbulent flow, better U. I concluded the difference has to be because of the plate gaps, but i am not certain. I do not have plate gap information, but i did request it...pending still.
I tried to do a preliminary verification of bidder A's design to estimate a range of U by modelling the flow as a rectangular duct with a very large aspect ratio, and using his dimensions. It didnt work. The answer i got was in the order of 0.5 kW/m2C.
Moreover, it is hard to believe that a vendor has a HX four times better than the other, especially when the liquids are the same and the plate material and thickness is the same.
Can anyone tell me a rough idea of the U value of this application. Where can I see past examples of HX's used so that I can believe bidder A. I want to believe bidder A!
Thanks