Dear Friends,

We are supplying a 400 SQ.MM Bare Copper Conductor (Hard Drawn - HDCC) for Customer Substation Application for Busbars and Jumper Connection. Any idea how to get this data? I think PLS - CADD has similar interface.

Capture_em2aiy.jpg


Thanks
Chris
 
Replies continue below

Recommended for you

Are you using copper cable under tension? If this is only for flexible jumpers, most of the parameters may not be needed.

If this is for a common cable type, may have the parameters. Otherwise you (or the manufacturer) can send a chunk of the cable to a testing lab.
 
The offered 400sqmm Bare copper conductors are used for substation Busbar arrangement and equipment jumper connection. The Copper Conductor we offer is Soft.

59/2.92mm (Strand/Dia of strand)

Do I need to look into one of these right: ? So then 400 Sq.mm = 789.4 kcmil right?

Exact copper conductor with 59 strands is not available. I am asking for help because dont have license

Thanks
Chris
 
I tried that, I didnt understand how exactly to open that data?
 