We've run situation where I'd like some opinions. In a detail like the attached, the height of the plug weld slots are sized per Sec J2.3a which specs a min height of the thickness of the outer pipe plus 5/16". So for a 1/2" pipe those slots should be 13/16" minimum. A thicker wall pipe (5/8" instead of 1/2") was substituted and the slots were not adjusted accordingly.
The field welding inspector noticed the discrepancy and wrote an NCR. The welds were completed and inspected with the smaller slots.
Clearly the welds don't meet the specification. The commentary essentially says that the minimum sizes are to provide geometry that is conducive to good fusion and to avoid deep, narrow holes.
How much (if any) of these plug welds is usable? Should they be disregarded completely? Should the effective width be reduced to 9/16" (1/8" subtracted from each side)? Should the welds be UT and if that passes call them good? Should I call them good because they were inspected during installation and there were no issues with access?
Any opinions are welcome.
The field welding inspector noticed the discrepancy and wrote an NCR. The welds were completed and inspected with the smaller slots.
Clearly the welds don't meet the specification. The commentary essentially says that the minimum sizes are to provide geometry that is conducive to good fusion and to avoid deep, narrow holes.
How much (if any) of these plug welds is usable? Should they be disregarded completely? Should the effective width be reduced to 9/16" (1/8" subtracted from each side)? Should the welds be UT and if that passes call them good? Should I call them good because they were inspected during installation and there were no issues with access?
Any opinions are welcome.