Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pole loading load cases 1

Status
Not open for further replies.

gwillis33

Electrical
Aug 18, 2015
9
0
0
AU
When doing a pole load calculation (ie nett load on pole due to conductor loads) what are common load cases you'd look at? eg no wind @ 60deg, wind/ice @ 0 deg etc?
Thanks.
 
Replies continue below

Recommended for you

It depends on the place you're doing the project. In the US, NESC defines three different zones: Light loading, Medium loading and Heavy loading. Light loading - 0" ice, 4psf wind, Medium loading - 1/4" ice, 4psf wind, Heavy loading - 1/2" ice, 4psf wind. You can find the NESC zones map in NESC book 2012 edition or a Google search might help you figure out which loading zone your current work falls under.
 
Thanks engratcorner. Let's say you are in the heavy loading zone. Would you examine pole loading under the heavy load case, and also under a no wind case?
 
Status
Not open for further replies.
Back
Top