I have a project where an engineer used an in-house procedure to check some long span roof joists for ponding loading.
The roof uses primary drains only and then depends upon over-the-roof flow of water to scuppers at a far end of the building. There are about 4 to 5 valleys that have these primary drains and the water must flow over the various ridges which about 3" high or so, to get to the scuppers.
I honestly don't know what the exact procedure is but I think it is essentailly this:
1. Load up the roof joist with the initial water assuming the drain is clogged.
2. The joist deflects downward some initial amount.
3. Recalculate the new depth of water based on the now-deflected shape of the joist.
4. Re-calculate the new deflection of the joist based on the re-calculated depth of water.
5. Repeat until convergance.
I don't know the validity of this process.
I checked the joists against AISC for ponding (9th Edition and second Edition section K2 or Appendix 2 in the new 13th Edition). This check revealed that the joists were no good in terms of ponding control.
However, the engineer states that the AISC provisions only determine IF you need to further check for ponding....not whether there is a problem with ponding. He claims that his method above then satisfies the code with respect to ponding.
The actual language that AISC uses is: [blue]The roof system shall be considered stable for ponding and no further investigation is needed if both of the following two conditions are met:....[/blue]
This seems to imply a "further investigation".
I've never thought of it like this before. I've always taken the AISC provisions as determining if the joists are inadequate for ponding or not.
I've never heard that they simply determine whether a further check is required.
Thoughts on this?
The roof uses primary drains only and then depends upon over-the-roof flow of water to scuppers at a far end of the building. There are about 4 to 5 valleys that have these primary drains and the water must flow over the various ridges which about 3" high or so, to get to the scuppers.
I honestly don't know what the exact procedure is but I think it is essentailly this:
1. Load up the roof joist with the initial water assuming the drain is clogged.
2. The joist deflects downward some initial amount.
3. Recalculate the new depth of water based on the now-deflected shape of the joist.
4. Re-calculate the new deflection of the joist based on the re-calculated depth of water.
5. Repeat until convergance.
I don't know the validity of this process.
I checked the joists against AISC for ponding (9th Edition and second Edition section K2 or Appendix 2 in the new 13th Edition). This check revealed that the joists were no good in terms of ponding control.
However, the engineer states that the AISC provisions only determine IF you need to further check for ponding....not whether there is a problem with ponding. He claims that his method above then satisfies the code with respect to ponding.
The actual language that AISC uses is: [blue]The roof system shall be considered stable for ponding and no further investigation is needed if both of the following two conditions are met:....[/blue]
This seems to imply a "further investigation".
I've never thought of it like this before. I've always taken the AISC provisions as determining if the joists are inadequate for ponding or not.
I've never heard that they simply determine whether a further check is required.
Thoughts on this?