Hi all,
We're getting a much lower power factor than anticipated on a 100 kW asynchronous generator intended for 100% power export to the grid. It is connected via a dedicated line that serves only this generator and it's auxiliary systems (about 5 kW worth of 3 phase motors).
This is a follow up of thread237-376121, please see that thread for details. Please note that we added a power reactive power control to the configuration described in the previous thread. This power factor controller was designed so it would bring the power factor to 0.95 from the 0.85 figure this machine has at 100 kW
A power analyzer on-board the genset recorded the following, while the reactive power control was on-line
Real power: 54.7 kW
Apparent power: 80.3 kVA
Reactive power: 62.2 kVAR
PF: 0.63
The generator is rated at 0.73 @ 50kW with no reactive power control. Why is the PF so poor?
Thanks and regards,
Ernesto.
We're getting a much lower power factor than anticipated on a 100 kW asynchronous generator intended for 100% power export to the grid. It is connected via a dedicated line that serves only this generator and it's auxiliary systems (about 5 kW worth of 3 phase motors).
This is a follow up of thread237-376121, please see that thread for details. Please note that we added a power reactive power control to the configuration described in the previous thread. This power factor controller was designed so it would bring the power factor to 0.95 from the 0.85 figure this machine has at 100 kW
A power analyzer on-board the genset recorded the following, while the reactive power control was on-line
Real power: 54.7 kW
Apparent power: 80.3 kVA
Reactive power: 62.2 kVAR
PF: 0.63
The generator is rated at 0.73 @ 50kW with no reactive power control. Why is the PF so poor?
Thanks and regards,
Ernesto.