Due to the space restriction and the position of the air condition box in the vehicle, I have no choice but position the evaporator horizontally.
(Typically, in all automotive vehicles position the evaporator vertically- tank at the top or bottom that will allow the air to pass through the evaporator side ways –
on the other hand, horizontal position, the air will pass from the bottom upward.. I hope it is clear)
The evaporator tested vertically and horizontally with the same conditions:
Here's a very brief summary of the findings:
- No instability was observed at 150 or 250 cfm @ 90 degree position.(vertically)
- Instability was observed at 150 and 250 cfm @ 0 degree position (horizontally)suction pressure was all over the map from 10 PSI to 40 PSI..
- The 0 degree horizontal position had 1000 BTU/hr lower performance than the 90 degree vertical position.
The questions are:
Why I experienced instability at 0 degree horizontal position?
Is it common to loss performance by set the plate and fin evaporator horizontally?
Test details:
Refrigerant Inlet temperature 120F
Superheat 8-12F
Suction pressure 25PSI
TXV pressure (head) 200 PSI
Air inlet temp. 90F
Relative humidity 50%
Air flow 250
(Typically, in all automotive vehicles position the evaporator vertically- tank at the top or bottom that will allow the air to pass through the evaporator side ways –
on the other hand, horizontal position, the air will pass from the bottom upward.. I hope it is clear)
The evaporator tested vertically and horizontally with the same conditions:
Here's a very brief summary of the findings:
- No instability was observed at 150 or 250 cfm @ 90 degree position.(vertically)
- Instability was observed at 150 and 250 cfm @ 0 degree position (horizontally)suction pressure was all over the map from 10 PSI to 40 PSI..
- The 0 degree horizontal position had 1000 BTU/hr lower performance than the 90 degree vertical position.
The questions are:
Why I experienced instability at 0 degree horizontal position?
Is it common to loss performance by set the plate and fin evaporator horizontally?
Test details:
Refrigerant Inlet temperature 120F
Superheat 8-12F
Suction pressure 25PSI
TXV pressure (head) 200 PSI
Air inlet temp. 90F
Relative humidity 50%
Air flow 250