crthompson
Electrical
- Aug 8, 2011
- 75
I have recently been introduced to Transient Recovery Voltage issues when a vacuum contactor clears a fault. We had a failure of some lightning arresters in the field and some of the engineers think that it is a TRV issue. I have a basic understanding of what occurs when a vacuum contactor clears a fault and how this causes problems. My question is this: Can a TRV travel from a 4160V secondary on a XFMR to a 995V secondary on the same XFMR? The 4160V secondary has its own lightning arresters at the XFMRs terminals and so does the 13,800V primary. The 4160V secondary has several heavy inductive loads controlled by vacuum contactors. When the fault occured, the 995V circuits were energized to the line side of the MCCBs but they weren't closed. We had 3 lightning arresters (each phase to ground on a high resistance grounded system)these were installed on the line side of the 995V MCCBs within a couple of feet. There is also a reactor on each phase of the 995V circuits between the XFMR and the MCCBs. These arresters failed very violently and caused a subsequent 3 phase to ground fault on the line side of the MCCBs. I would also be grateful if any of you could share any other ideas as to what may have caused this. Thanks in advance.