This is less a engineering question and more a product question. I have someone wanting to anchor to an existing 3" thick, light-weight slab in seismic design category D (cracked concrete). I can't find any anchor that is tested in anything less than 3.25" (1/4" Hilti KB-TZ2). LRFD shear load per anchor is very small (70 lbs) and no uplift. It's such a small load, I'm not worried about any anchor that is decided upon, but showing it to work on paper is something else. So any products that I can use in light-weight cracked concrete that is only 3" thick?

If not, I was thinking about using an anchor rated for use in CMU thinking that would be conservative and hoping the AHJ wouldn't argue?

Juston Fluckey, SE, PE
Engineering Consultant
 
Have you tried looking at Hilti KH-EZ Screws? You can get the 1/4" to work in ~2" of concrete and they are rated for seismic applications.
 
Enable said:
Have you tried looking at Hilti KH-EZ Screws? You can get the 1/4" to work in ~2" of concrete and they are rated for seismic applications.

Looking at ESR-3027, the 1/4" anchor requires 3.25" thickness:
Capture_ykdk1i.jpg


Juston Fluckey, SE, PE
Engineering Consultant
 
My apologies. I erroneously assumed given the thickness and light-weight concrete that this was concrete over a metal deck, which only requires a minimum thickness of 2-1/2" for the 1/4" KH-EZ. Nothing else comes to mind unfortunately.
 
Hilti HDI-P TZ might work: Link. If not, perhaps you can justify with a load test. Here's a thread dealing with a similar situation: thread507-361097.
 
Deker,
Thanks! That one looks promising. I'll pursue that one if the client comes back and confirms the 3" thickness. They told me 3" but they originally said 4". So I just want to make sure they don't really have a little more than 3" which would solve everything.

Juston Fluckey, SE, PE
Engineering Consultant
 