This question is specific to industrial facilities with lots of mechanical/process equipment. I have seen a divide in whether structural engineers feel post Installed anchorage for equipment needs to be shown and called out on drawings.
What opinions are there on this?
I have typically been taught to always show post Installed anchorage for equipment. This includes calling out the diameter, anchorage, embed, projection and location just the same as cast in place.
I understand that equipment anchors are installed after the equipment is in place, so locating is not necessary - but for me it is useful to coordinate rebar/foundation size. I also can't understand not showing it at all since otherwise how is it sized or bid by a contractor.
Thoughts?
It depends. Is the design of the anchorage in my scope? If yes, then I'll show it on my drawings. If the anchorage of the machine is by others...then I'll show something, I won't dimension it, and I'll point to it and say "machine anchorage by others" or some such.
I would prefer to show post Installed anchorages. ( The post installed anchors installed by mechanical crew after the equipment is in place, ) In order to make sure the required edge distances are provided, it will be necessary to show ..
Say my experience..
Use it up, wear it out;
Make it do, or do without.
NEW ENGLAND MAXIM
This right here.
Why...
So much...
White Space? @HTURKAK
Shown but usually not located. Noted as field locate, min edge distance xxx. If I knew where the anchors were going to go they would be cast in
All information is needed for post installed anchors except the location can be noted as field verify/locate.
You will either get an RFI or some construction contractor will just install whatever.
I work in a refinery and monitor construction everyday.