Post Installed Anchors

Status
Not open for further replies.

Mecseji

Structural
Nov 1, 2023
1
This question is specific to industrial facilities with lots of mechanical/process equipment. I have seen a divide in whether structural engineers feel post Installed anchorage for equipment needs to be shown and called out on drawings.

What opinions are there on this?

I have typically been taught to always show post Installed anchorage for equipment. This includes calling out the diameter, anchorage, embed, projection and location just the same as cast in place.

I understand that equipment anchors are installed after the equipment is in place, so locating is not necessary - but for me it is useful to coordinate rebar/foundation size. I also can't understand not showing it at all since otherwise how is it sized or bid by a contractor.

Thoughts?

 
Replies continue below

Recommended for you

It depends. Is the design of the anchorage in my scope? If yes, then I'll show it on my drawings. If the anchorage of the machine is by others...then I'll show something, I won't dimension it, and I'll point to it and say "machine anchorage by others" or some such.
 


I would prefer to show post Installed anchorages. ( The post installed anchors installed by mechanical crew after the equipment is in place, ) In order to make sure the required edge distances are provided, it will be necessary to show ..


Say my experience..







Use it up, wear it out;
Make it do, or do without.

NEW ENGLAND MAXIM


 
phamENG said:
Is the design of the anchorage in my scope? If yes, then I'll show it on my drawings.

This right here.

Why...










So much...






White Space? @HTURKAK
 
Shown but usually not located. Noted as field locate, min edge distance xxx. If I knew where the anchors were going to go they would be cast in
 
All information is needed for post installed anchors except the location can be noted as field verify/locate.
You will either get an RFI or some construction contractor will just install whatever.
I work in a refinery and monitor construction everyday.
 