Hello, many great threads here for rack post loading on slabs on grade. However, I can't seem to find answers to my specific questions.
1. I have an existing 7in slab that I am evaluating for post load of 7500 lb often time back to back with another equally load post.
1. I have an existing 7in slab that I am evaluating for post load of 7500 lb often time back to back with another equally load post.
1a. Using the ringo and anderson book, which gives a few methods, I typically use the PCA charts method for new design. However, for this scenario It suggests a slab larger than 7in.
2. I can avoid every saw cut joint. So I might have a post load within a couple feet from an interior (interior to my overall 50ft x 56ft bay surrounded by construction joints) sawcut joint. The joint has a 1 in saw cut and #3@15s continuous through the joint.
2. I can avoid every saw cut joint. So I might have a post load within a couple feet from an interior (interior to my overall 50ft x 56ft bay surrounded by construction joints) sawcut joint. The joint has a 1 in saw cut and #3@15s continuous through the joint.
2a. When evaluating a post load, should I reduce the thickness by the 1" saw cut so I can count on the slab to transfer the load through the joint?
3. The charts for load back to back were giving a slab thicker than 7in, however, many people online have said a forklift would typically control the slab thickness, so I feel like I am doing something wrong in my efforts because I definitely get the post load to be the controlling factor.
3. The charts for load back to back were giving a slab thicker than 7in, however, many people online have said a forklift would typically control the slab thickness, so I feel like I am doing something wrong in my efforts because I definitely get the post load to be the controlling factor.
3a. I decided to evaluate as a beam on elastic foundation with free edges and this gets me close, but not when I reduce the thickness by the 1in saw cut. So again, left wondering, do I need to do this reduction in order to transfer load across the saw cut joint?
4. At the construction joints the detailing is a #3 dowel at 24" and a diamond dowel alternating with the #3 dowel at 24" OC. This doesnt match the ACI 360 recommendations. I am used to using Yoder & Witczak, "Principles of Pavement Design" for evaluating load transfer across doweled joints but this layout doesn't fall within the limits of the procedure in this reference.
4. At the construction joints the detailing is a #3 dowel at 24" and a diamond dowel alternating with the #3 dowel at 24" OC. This doesnt match the ACI 360 recommendations. I am used to using Yoder & Witczak, "Principles of Pavement Design" for evaluating load transfer across doweled joints but this layout doesn't fall within the limits of the procedure in this reference.
4a. This is why I decided to treat as a free edge in the beam on elastic foundation model
5. Has any relied on the approach in this article: ? It produces much higher slab capacities than any other method I have seen. The article assume there is no other post load within the relative stiffness radius but also, if I just say my loads are right on top of each other the capacity is sufficient. If this is the case, why isn't there more information out there using this approach in articles?
6. In the beam on elastic foundation model I am checking the slab moment demand against the cracking moment. Does this seem reasonable? If the slab cracks I assume it no longer has a mechanism for transferring the load across the slab. The positive moment is controlling and if it were to crack wouldnt it crack right below the post on the bottom side of the slab and that be a bad thing?
7. And for my final question; does 7in slab seem reasonable for a back to back 7500 post load? And if so, how do I get the numbers to validate it?
The bearing pressure is not exceeded and the punching shear is good as well.
5. Has any relied on the approach in this article: ? It produces much higher slab capacities than any other method I have seen. The article assume there is no other post load within the relative stiffness radius but also, if I just say my loads are right on top of each other the capacity is sufficient. If this is the case, why isn't there more information out there using this approach in articles?
6. In the beam on elastic foundation model I am checking the slab moment demand against the cracking moment. Does this seem reasonable? If the slab cracks I assume it no longer has a mechanism for transferring the load across the slab. The positive moment is controlling and if it were to crack wouldnt it crack right below the post on the bottom side of the slab and that be a bad thing?
7. And for my final question; does 7in slab seem reasonable for a back to back 7500 post load? And if so, how do I get the numbers to validate it?
The bearing pressure is not exceeded and the punching shear is good as well.