Hey All,
Doing an evaluation of an existing building constructed around 2006 and there is an irregular condition at one of the exterior cantilevered balconies.
1) They ran a pour strip through a portion of the balcony. Balcony is about 11' wide total and there is 6' on one side of pour strip, 3' wide pour strip, and 2' on the other side.
2) On the 6' wide side of the balcony, there's 7 PT tendons being terminated near the corner of the balcony. Obviously none in the pour strip and none in the 2' side of balcony.
This has resulted in a balcony that is noticeably jacked up on one side and there is a crack running perfectly along where the pour strip meets the 2' wide side of the balcony. (Photos attached). And it looks like they cut a control joint in the bottom of the slab up to the drip edge.
My initial evaluation is that this is a case of poor engineering judgement resulting in some bad upwards deflection, but this is really not a life safety issue and now that initial deflection and much of the long term deflection is worked out it's not going to get a whole lot worse over time. And I think actually trying to fix anything will create more issues than it solves. We're basically going to repair and seal the crack and put a sloped traffic coating to fix the drainage.
I wanted to tap into this community and see if you all agreed with my evaluation or if you would recommend anything different in this case?
Background info:
Unbonded PT slab, building is located in the Pacific Northwest




Doing an evaluation of an existing building constructed around 2006 and there is an irregular condition at one of the exterior cantilevered balconies.
1) They ran a pour strip through a portion of the balcony. Balcony is about 11' wide total and there is 6' on one side of pour strip, 3' wide pour strip, and 2' on the other side.
2) On the 6' wide side of the balcony, there's 7 PT tendons being terminated near the corner of the balcony. Obviously none in the pour strip and none in the 2' side of balcony.
This has resulted in a balcony that is noticeably jacked up on one side and there is a crack running perfectly along where the pour strip meets the 2' wide side of the balcony. (Photos attached). And it looks like they cut a control joint in the bottom of the slab up to the drip edge.
My initial evaluation is that this is a case of poor engineering judgement resulting in some bad upwards deflection, but this is really not a life safety issue and now that initial deflection and much of the long term deflection is worked out it's not going to get a whole lot worse over time. And I think actually trying to fix anything will create more issues than it solves. We're basically going to repair and seal the crack and put a sloped traffic coating to fix the drainage.
I wanted to tap into this community and see if you all agreed with my evaluation or if you would recommend anything different in this case?
Background info:
Unbonded PT slab, building is located in the Pacific Northwest