Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

POST TENSIONED SLAB DESIGN

Status
Not open for further replies.

RamiHabchi93

Civil/Environmental
Jan 22, 2017
26
Hi, In post tensioned slab design, the serviceability requirements(fc<0.6f'c..etc) are applied even if I put reinforcement in the slab?
 
Replies continue below

Recommended for you

Yes. Depending on the code that you are required to use, there will be tensile and compressive stress limits at both 'transfer' and 'in-service', and generally (depends on the code) they must be checked and satisfied even if you place mild steel bonded reinforcement.

When it comes to checking flexural tensile stresses at service, the type of slab will determine the extent of allowable flexural tension (eg one-way slab vs flat plate). Some codes refer to class "U", "C" and "T", for uncracked, cracked and transition, other codes have different nomenclature depending on the exposure, type of slab etc.

Strength requirements for minimum bonded reinforcement must also be satisfied.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor