POST TENSIONING GROUT STRENGTH FOR TENDON THAT PASSING THROUGH COLUMN/WALL

Status
Not open for further replies.

aimansuo

Civil/Environmental
Jul 12, 2022
1
Hi I'm from Malaysia and new to post tensioning.

I'm working with bonded systems flat slab with drop panel and the tendon arrangement mostly is banded/distributed type. So some tendon are required to go pass through column and shear wall. I'm looking for explanations whether the grout strength for tendons that are passing through column/shear wall shall be of the same strength/grade with columns/shear walls. I'm finding hard time finding this information. Does anyone knows where I can refer this? Fyi the slab concrete grade is 35mpa and the columns/shear walls is 40mpa.

Thanks.
 
Replies continue below

Recommended for you

With a strength difference of only 5MPa it won't be a problem.

More generally you should check the transmission of axial force through the floor if there is a large difference in strength grade between the column and the slab. This should be covered in your design Code.
 
Concrete grout strength is not really controllable. It is normally about 40MPa.

On another note, it is completely illogical to use banded/distributed with a flat slab and drop panels. It you are using the PTI full Panel Width design approach for this it is rubbish (as are a couple of Text Books and Manuals that suggest the approach)! You are grossly over estimating the capacity in the distributed direction.
 