1-800 Roberto
Structural
- Apr 16, 2021
- 2
I have an issue with a F1554 Grade 55 anchor bolt that is supposed to see only tension due to uplift (interior column of a PEMB). I am the EOR on the foundations of this project where a sub bent one bolt about 15 to 20 degrees. The GC was able to bend it back, but I am aware that AISC does not allow bending back for this grade. My solutions are three,
1. To cut and weld back if the F1554 Gr 55 per AISC guidelines provided it meets supplement S1.
2. To cut it and use a coupler if it fits in the grouted space under the base plate which is 2"
3. To drill and epoxy another bolt in the proximity (about 4" away from the bent one if the PEMB allows it) and leave the bent-back bolt in place but render such bolt as non existing for uplift purposes. The Ultimate uplift is in the order of 46 kips distributed among (4) 3/4" bolts. No shear, and no overturning.
Any suggestions or comments?
1. To cut and weld back if the F1554 Gr 55 per AISC guidelines provided it meets supplement S1.
2. To cut it and use a coupler if it fits in the grouted space under the base plate which is 2"
3. To drill and epoxy another bolt in the proximity (about 4" away from the bent one if the PEMB allows it) and leave the bent-back bolt in place but render such bolt as non existing for uplift purposes. The Ultimate uplift is in the order of 46 kips distributed among (4) 3/4" bolts. No shear, and no overturning.
Any suggestions or comments?