Unfortunately, with the exception of North America and a few other markets, most of the world uses IEC rated equipment. I suspect that in reality, most vendors meet the accuracy at 0 burden (I know my company does), but unless it's spelled-out in the customer's specification, you won't know for sure.
To make matters worse, for high-voltage units, it is common to see winding burden ratings in excess of 200 VA, meaning that by the letter of the standard, unless they have the winding loaded to 50 VA, then they're not assured to meet the accuracy class. As stated above, in an HV installation, VT rarely see above 5 VA, and that's with a string of relays and meters connected to them!