Potential Transformer Primary Fuse Basis for Sizing 2

Status
Not open for further replies.

brainsalad

Electrical
Apr 16, 2012
33
Greetings:

Would be grateful for your thoughts regarding the origin of any bases used for the inrush capability of primary fuses for potential transformers.

I have a GE JVM-3 PT (2400-kV, 750-VA) with an EJ-1 fuse. Also an ancient ITE PT-6 PT (600-VA, 480-V) with Gould A6Y7E-96 fuses......

Can anyone recall the origin or basis of the requirement to have primary fuses tolerate at least 12x (or 25x) rated primary current?

Thanks for your help.
 
Replies continue below

Recommended for you

Guys-

The HV fuses for PT's aren't there to protect the PT. they're in the circuit to prevent a PT fault from affecting the source switchgear/buswork.

old field guy
 
All:

Thank you for your contributions.

I first set out to answer my original question, "[What is] the origin or basis of the requirement to have primary fuses tolerate at least 12x (or 25x) rated primary current?", but have been delighted in learning more than I have wondered.

After searching, one answer to my original question is found in IEEE-242 (Buff Book), which describes the basis for that requirement as derived from the "hot-load pickup" phenomenon, which requires magnetizing inrush points at 14x FLA at T=1s and 28x FLA at T=0.01s.

A nice article on the subject (but not necessarily for PTs):
Now wondering "why not" the same criteria for 480-V PTs (above is all medium voltage).....
 