Pour over existing slab

Status
Not open for further replies.

braka

Structural
Jul 30, 2003
1
I have a 100,000 square foot facility 30 feet high, that has sloping floors. I need to make it level for racking systems and to be able to run a fork lift that can unrack at a height of 28 feet. One way is to put crushed stone over the existing floor area and pour at least a 6" slab over it to get the proper floor load ratio for this use. The problem is it will cost me $4.00 per square foot or $400,000. Are there any other materials or methods that I can use to make the job less expensive without sacrificing the floor load ratio or the longevety of the floor.

Thank you
 
Replies continue below

Recommended for you

You could use a bonded topping slab on the existing slab. This involves preparing the existing surface by shotblasting and then placing the topping slab, perhaps 2 to 3 inches thick, over the existing. New control joints should match the existing control joints.
 