waytsh
Structural
- Jun 10, 2004
- 371
Has anyone else used or seen a poured concrete frost wall without a footing? I am performing a peer review where this was done on with an 8" thick concrete wall supporting 8'-16' of masonry block wall above. The walls extend about 4' into the ground and are on a crushed stone base. The wall is reinforced like a wall and not a grade beam, i.e. there are no stirrups and just uniformly distributed vertical and horizontal bars. The wall is not supporting any column loading.
Wouldn't Section 1809.4 of the IBC Code requiring a minimum footing width of 12" apply? I know something similar is commonly done is the residential industry with precast concrete panels but I have never seen it commercially.
Wouldn't Section 1809.4 of the IBC Code requiring a minimum footing width of 12" apply? I know something similar is commonly done is the residential industry with precast concrete panels but I have never seen it commercially.