Trublmkr
Electrical
- Apr 13, 2011
- 6
I have a power panel that is fed by 208 3 phase coming from a UPS and a second or alternate power feed from the city utility line, they are synced and within a fraction of a volt of each other. Does anyone know why if the load is measured with a clamp on meter, why when the feeds are sharing the load they read 60% to 75% higher. If 1 feeder is connected and the other not we see approximately 40 amps per leg, but when they are both on and should be sharing the load, 1 feeder shows 50 to 60 amps per leg and the other feeder shows 70 to 90 amps per leg. But when we check Power Logic it reports the load at 40 amps each. Does anyone have an explanation of what could be happening here? We have this same thing happening in at least 2 different buildings. It is not causing any problems, we just can't figure what would cause this. Thanks for your time.