rhatcher
Electrical
- Jan 17, 2001
- 636
I want to install power factor correction at my facility. I have a single 13.8kV feeder with utility meter feeding 7 substations with various low voltage secondaries. I would like to install one capacitor bank on the secondary of one the the substations to compensate for the entire facility. I have examined several months worth of power data (15 minute interval) and determined that my kvar consumption varies between 150 and 300, with 200 being the nominal value for most of the time, 300 being rare, and 150 occurring about 25% of the time. There are no drives or sensitive electronics (other than PC's) on the system. I want to install a 200kVAR capacitor bank on the secondary of one of the transformers (3000kVA) to achieve near unity power factor during normal operations (about 75% of the time). This means:
- 25% of the time I will have a leading power factor for the entire facility (meaning at the 13.8kV feeder).
- 100% of the time the secondary bus of the 3000kVA transformer where the capacitor is installed will have a leading power factor.
(If you are noting a discrepancy then you are right. I have about 8MVA of capacity but my average consumption is only 250-300kVA. Why that it true is a long story that is off-topic)
My questions are:
- Will the leading power factor cause overvoltages on the substation secondary where the cap is installed or on the 13.8kV feeder? My feelings are that the 200kVAR cap is orders of magnitude smaller than the capacity of the transformer or the feeder so there should be no effect. Am I right?
- What are the general pitfalls (hazards) of running a leading power factor? (There is no penalty from the utility).
- 25% of the time I will have a leading power factor for the entire facility (meaning at the 13.8kV feeder).
- 100% of the time the secondary bus of the 3000kVA transformer where the capacitor is installed will have a leading power factor.
(If you are noting a discrepancy then you are right. I have about 8MVA of capacity but my average consumption is only 250-300kVA. Why that it true is a long story that is off-topic)
My questions are:
- Will the leading power factor cause overvoltages on the substation secondary where the cap is installed or on the 13.8kV feeder? My feelings are that the 200kVAR cap is orders of magnitude smaller than the capacity of the transformer or the feeder so there should be no effect. Am I right?
- What are the general pitfalls (hazards) of running a leading power factor? (There is no penalty from the utility).