Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Power factor correction of motor 1

Status
Not open for further replies.

fornhamspark

Electrical
Oct 23, 2004
44
can anybody please advise me on power factor correction of a star/delta started motor.

my question is that should the capacitor be switched in with the main contactor or the delta contactor, and from what size of Kvar is it advisable to use a contactor.


Cheers All


 
Replies continue below

Recommended for you

Switch the capacitors in with the delta contactor.

There is an advantage with the Y/D starter when it comes to compensation; the motor doesn't stay connected when you switch off. Or rather, the "other end" opens so there is no risk of overexcitation of the motor when you deenergize it. That often happens when you switch off a wye or delta connected motor with the capacitors in-circuit and they are a bit on the high side.

The star time is so short that you needn't bother about compensation then - the pf is also beyond compensation during start.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor