Hi
Can anyone advise?
I have 2 motors which is rated at 0,75 kw each and 3 amp connected in series and a power flex 40 with a 6 amp max current rating.
The current limit setting on the drive is 6A.
The problem that I am experiencing is when the motor starts up to 70% it tripped with an F12 h/w over current fault, I measure the amps to be below 2.5A when it trips, I have replaced the motors and the drive .
Any further ideas
Thank you