As the engineer of record, what would be your typical checklist for line walk down before giving the go-ahead for energization?
I think other than obvious items like phasing looks correct, poles are not bending etc EOR can't really check anything else. Maybe its best to get signed record of inspection from the contractor with the confirmation that
1) All the assemblies are installed as per the engineering drawings.
2) sags are in accordance with the tables and that ground clearances comply with design requirements.
3) phasing is correct.
4) temporary safety grounds are removed.
5) all bolts and nuts are tight.
I'll appreciate any thoughts on this.