Mary12345

Electrical
Dec 28, 2016
2
I have a 480V 50A Breaker, with a transformer 480V/120V that's 25kVA, and a power panel pulling 15A.
Can I add another power panel to the transformer pulling 50A if I increase the main breaker to 100A?
If not, then what's my limiting factor the transformer or the breaker?
 
Replies continue below

Recommended for you

Code requirements are the limiting factor. Check the NEC.
From your description, I strongly suspect that your present installation is not in compliance.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Like Davidbeach said, what does your calculations say?

I suspect the max CB allowable for your TX is 50A. i doubt you can increase it to 100A. You might have to increase the TX size, but again, that depends on your calc/studies. If you do, remember you need to make sure your Panel and your cables are rated for the new ampacity of 100A.
 
I would say that the breaker is your limiting factor as your secondary side can handle 122 amps.
 
Mary -
Let's get a little bit clearer on the system: We got "480/120", "3 phase", "25kVA".

I've never seen a 25kva, 3ph transformer. That is a single phase size. 3ph would be 30kva.

If the system (transformer and panel, not the 480V feeder) is 1ph, then I would expect 480/240/120

If 3ph, then 480/208/120.

Of course you could have 1ph, 480/120. Not very common, but there are some.

So, what is the system?