IEEE Std C62.21-2003, “IEEE Guide for the Application of Surge Voltage Protective Equipment on AC Rotating Machinery 1000 V and Greater” states:
Has anyone heard of this configuration... shielded power system cable with shield grounded at one end only?
I assume you still have stress cone on the other end, but it just has no external ground connection
What concerns would you have for this configuration?
=====================================
(2B)+(2B)' ?
A.4 Summary of motor starting surge levels and surge rise times
Given a maximum [theoretical] prestrike voltage on third pole closing of 2.82 pu, the steep-fronted motor terminal surge can vary between 2 pu and 5 pu depending on the configuration. The highest surges are associated with small motors fed by shielded cables grounded at both ends with a large number of other loads present on the motor-starting bus. The most effective mitigation measure is to ground only the motor end of the shield.
The calculated surge rise time, using time constants, can range from 50 to 1500 ns depending on the configuration. The fastest rise times are associated with small wye-connected motors, short shielded XLPE or EPR cables, and narrow width switchgear (short bus length at the supply end).
Has anyone heard of this configuration... shielded power system cable with shield grounded at one end only?
I assume you still have stress cone on the other end, but it just has no external ground connection
What concerns would you have for this configuration?
=====================================
(2B)+(2B)' ?