Does anyone have a good reference on estimating or calculating power system capacitive charging current in order to apply system ground fault protection in medium voltage applications?
 
Replies continue below

Recommended for you

An empiric equation which could be used to calculate the current flowing through the cable capacitance is
I = 0.2 * U * length
where
"I" is the capacitive current in A
"length" is the cable length in kilometers
"U" is the cable rated voltage in kV
It could be interesting to know how long such current lasts.
Usually to avoid spurious trips a 0.2 s delay is used for the ground elements
 
One could also use an EMTP-type program to model the cable and observe the charging current. An example program would be ATP (Alternative Transients Program) - it is free though a little learning curve is required. I used it in a college class and this is one of the things that we used it for.
 