Power Transformer 300/150/150MVA cooling type. 3

slavag

Electrical
May 15, 2007
2,041
Dear Colleagues.
What is preferable cooling type of Power Transformer 300/150/150MVA 161/33/33kV? It will be Step-Up transformer. Generation type : PV and BESS.
ONAN/ONAF
ONAN/ONAF/OFAF
ONAN/ONAF/ODAF

Thanks a lot in advance!
 
Replies continue below

Recommended for you

The ideal arrangement is ONAN/ ONAF . In case you have any restrictions in foot print, go for ODAF cooled compact coolers.
 
In case of ONAN/ONAF we use 0.6..0.7/1 Sonan / Sonaf.
What is recommendation for ONAN/ODAF?
 
It is ODAF only without any ONAN. Each cooler of 20-25 % rating will be provided with a standby spare cooler.
 
Dear PRC
Thanks a lor for your help!
 