I have a 3ph 2700KVA continuous rating or 12677KVA pulsed at 36KV/670V transformer, I received the test results sheet from the manufacturer and I am trying to go trough the calculations to check it out. They also kindly supplied the formulas that they use for their calculations.
The problem I have is the I^2R losses calculations. I got the resistance measured for each winding (primary and secondary) so according to their formulas I should start by getting the resistance for the primary and secondary. The formulas given are:
For a delta connection which the primary is, R should be the sum of the resistances divided by 2.
For a Star connection which the secondary is, R should be the sum of the resistances divided by 6
Then the I^2R losses are calculated as, the sum of the Irms squared multiplied by the resistance. The way I have done it is to use the rated primary current squared multiplied by primary resistance and the secondary rated current squared multiplied by the secondary resistance and then I added the values together.
The problem is that the values do not tie in at all, so or they supplied the wrong values or I am doing something wrong. I favour the later as all the other calculations on the sheet match with my results when I use another method of calculating the values.
Any help is appreciated.
Best regards
Luis
I have a 3ph 2700KVA continuous rating or 12677KVA pulsed at 36KV/670V transformer, I received the test results sheet from the manufacturer and I am trying to go trough the calculations to check it out. They also kindly supplied the formulas that they use for their calculations.
The problem I have is the I^2R losses calculations. I got the resistance measured for each winding (primary and secondary) so according to their formulas I should start by getting the resistance for the primary and secondary. The formulas given are:
For a delta connection which the primary is, R should be the sum of the resistances divided by 2.
For a Star connection which the secondary is, R should be the sum of the resistances divided by 6
Then the I^2R losses are calculated as, the sum of the Irms squared multiplied by the resistance. The way I have done it is to use the rated primary current squared multiplied by primary resistance and the secondary rated current squared multiplied by the secondary resistance and then I added the values together.
The problem is that the values do not tie in at all, so or they supplied the wrong values or I am doing something wrong. I favour the later as all the other calculations on the sheet match with my results when I use another method of calculating the values.
Any help is appreciated.
Best regards
Luis