Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Power Transformer Control Boxes

Status
Not open for further replies.

foxhoundme

Mechanical
Sep 30, 2003
18
Is there a standard which speaks to the layout of controls in a power transformer junction box? Or are there general rules to which to follow for general layouts of components inside of a control box for large power transformers?
 
Replies continue below

Recommended for you

Depends where you are. In the UK the conductor and terminal numbering generally follows BEBS-12, or more latterly TS 50-19, numbering scheme. Both are published by the ENA. Physical arrangement generally just follows good industrial practice. Large organisations such as National Grid may have their own preferred arrangement, but they'll detail that in any purchase order.
 
The equipment will be located in North America region.
 
The IEEE standard is no more a draft standard and the final version has come as C57.148-2012 IEEE Standard for control cabinets for Power Transformers
 