Tony2802
Electrical
- Aug 24, 2022
- 6
The IEEE 141-1993 states that in general, the transformer inrush current is approximately 8 to 12 times the transformer full-load current for a maximum period of 0.1 s. However, in the IEEE 242-2001 only mention 12 times the transformer FLC. I see frequently engineer using 8 times FLC as inrush current. I could not really find a standard stating when to use 8 times or 12 times the FLC. On google, I found a document ( stating that transformers > 2500 kVA should use 12 times the FLC and < 2500 kVA should use 8 times the FLC. However, I could not find the standard or reference related to the 2500 kVA threshold for inrush current. Did you ever hear about this rule of thumb?