Power Transformers

Status
Not open for further replies.
Replies continue below

Recommended for you

Ask mfrs!! It also depends on duration of 'emergency' and load during "emergency". Bottom line is not to exceed temperature limit. There is no standard formula that I know of.

There have been instances of people trying to keep the transformer cool with garden hoses to keep the service going!!
 
I'm not an electrical engineer, but some one who has been given the task of finding this data based upon what appears on the name plate. Thanks anyway!
 
What is the size/type of the transformer (oil-filled? kVA?)



"The more the universe seems comprehensible, the more it also seems pointless." -- Steven Weinberg
 
Please look table 4 of IEC 60076-7 of 2005-12.Over Loading guide .It lists permissible emergency ratings for different type of trfs ( Distribution,medium and large) for different loading conditions viz Normal cyclic overloading, long time emergency loading,short time emergency loading.
 