Hi all,
i was involved with testing of a 7.5 MVA, 13.8kV-4.16kV transformer. the following points were noted.
1,The Liquid-Temp Indicator (thermometer)installed was with capillary and not direct stem type. Does ANSI C57.12.10 states that the Liquid-Temp Indicator (thermometer) shall be direct stem mounted in a closed well.Is it a violation of ANSI Standards?
2,The Load-Loss for the 7.5 MVA transformer was calculated by a computer program.this was done by injecting Approx 70% of the rated high voltage current. i.e. 219.6Amps instead of 313.77 Amps.Does ANSI C57.12.90 permit injecting only 70% instead of 100%, of the HV rated Current?
3,The oil analysis performed on sample taken from the 7.5MVA Transformer, did not give a satisfactory result. Four samples were taken from the same transformer and only one sample passed the Dielectric Voltage Breakdown test. The test was performed using ASTM-D877 test method. the sample which passed the test was kept undisturbed for an hour after the sample was taken and for the others the test was done immediately, after the sample was taken from the transformer. why is the oil which was kept for a while passing the test?
i need immediate help and request all the experts out there to help me out.
regards,
i was involved with testing of a 7.5 MVA, 13.8kV-4.16kV transformer. the following points were noted.
1,The Liquid-Temp Indicator (thermometer)installed was with capillary and not direct stem type. Does ANSI C57.12.10 states that the Liquid-Temp Indicator (thermometer) shall be direct stem mounted in a closed well.Is it a violation of ANSI Standards?
2,The Load-Loss for the 7.5 MVA transformer was calculated by a computer program.this was done by injecting Approx 70% of the rated high voltage current. i.e. 219.6Amps instead of 313.77 Amps.Does ANSI C57.12.90 permit injecting only 70% instead of 100%, of the HV rated Current?
3,The oil analysis performed on sample taken from the 7.5MVA Transformer, did not give a satisfactory result. Four samples were taken from the same transformer and only one sample passed the Dielectric Voltage Breakdown test. The test was performed using ASTM-D877 test method. the sample which passed the test was kept undisturbed for an hour after the sample was taken and for the others the test was done immediately, after the sample was taken from the transformer. why is the oil which was kept for a while passing the test?
i need immediate help and request all the experts out there to help me out.
regards,