Electrical1948
Electrical
- Apr 18, 2015
- 18
Hi all,
I was refreshing my symmetrical components theory and performed a calculation in Power factory (Digsilent) to compare against my calculations in Excel. I got all of the figures correct, however I am unable to calculate a zero sequence voltage component "through" a transformer.
The input data are as follows:
Operating voltage (Grid): UAN = 230 V <0 deg, UBN = 235 V < -120 deg, UCN = 240 V <120 deg
Transformer:
Rated voltage HV winding: 400V
Rated voltage LV winding: 400 V
Vector group: Dy11
I calculate the following symmetrical components on the HV side:
U+ = 235 <0 deg
U- = 2.887 < -150 deg
U0 = 2.887 < 150 deg
I calculate the following symmetrical components on the LV side:
U+ = 235 <30 deg
U- = 2.887 < 180 deg
I can't calculate U0 since I do not have the phase to neutral voltages. However, Powerfactory calculates U0 = 1.443 < 60 deg, which I do not understand.
Is there anyone who can explain how the U0 is calculated by Powerfactory?
I was refreshing my symmetrical components theory and performed a calculation in Power factory (Digsilent) to compare against my calculations in Excel. I got all of the figures correct, however I am unable to calculate a zero sequence voltage component "through" a transformer.
The input data are as follows:
Operating voltage (Grid): UAN = 230 V <0 deg, UBN = 235 V < -120 deg, UCN = 240 V <120 deg
Transformer:
Rated voltage HV winding: 400V
Rated voltage LV winding: 400 V
Vector group: Dy11
I calculate the following symmetrical components on the HV side:
U+ = 235 <0 deg
U- = 2.887 < -150 deg
U0 = 2.887 < 150 deg
I calculate the following symmetrical components on the LV side:
U+ = 235 <30 deg
U- = 2.887 < 180 deg
I can't calculate U0 since I do not have the phase to neutral voltages. However, Powerfactory calculates U0 = 1.443 < 60 deg, which I do not understand.
Is there anyone who can explain how the U0 is calculated by Powerfactory?