Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

PRC-005 Relay Monitoring

Status
Not open for further replies.

HamburgerHelper

Electrical
Joined
Aug 20, 2014
Messages
1,127
Location
US
Does anyone have any issues with getting the NERC PRC-005 maintenance 12 year window with having maintenance staff checking the relays periodically, like nightly. We don't have the relays connected to SCADA but someone should be regularly doing the rounds to check for equipment that has indicated that it has failed.

------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
Just replying to my own question with what I found if someone later searches for this.

The PRC-005 supplemental says this:

 "The alarming mechanism can be a standard alarming system or an auto‐polling system; the only
requirement is that the alarm be brought to the action‐site within 24 hours.   This effectively
makes manned‐stations equivalent to monitored stations.  The alarm of a monitored point (for
example a monitored trip path with a lamp) in a manned‐station now makesthat monitored point
eligible for monitored status."


------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top