MindofBarca
Structural
- Mar 7, 2013
- 36
All,
Good afternoon.
I have a precast concrete question regarding a podium style (precast beams, column, and hollow core) for two stories with stick framing above. One column, in particular, was cast too long; the precaster would like to salvage it if at all possible.
The column needs to be cut down 6". The top of column has cast-in coil inserts for precast beams to attach to and the column base has pockets with a 1" thick baseplate to sit on four exposed rebar cast into the footing.
ACI 318-11 7.10.5.7 has the top/bot tightly spaced tie criteria. Which we have met on both top and bottom, but once you remove either the top or the bottom 6", the next tie is 12"+ away.
Any thoughts or ideas on how to circumnavigate this criterion and properly trim down this precast column 6"?
Thanks in advance!
MindofBarca
Good afternoon.
I have a precast concrete question regarding a podium style (precast beams, column, and hollow core) for two stories with stick framing above. One column, in particular, was cast too long; the precaster would like to salvage it if at all possible.
The column needs to be cut down 6". The top of column has cast-in coil inserts for precast beams to attach to and the column base has pockets with a 1" thick baseplate to sit on four exposed rebar cast into the footing.
ACI 318-11 7.10.5.7 has the top/bot tightly spaced tie criteria. Which we have met on both top and bottom, but once you remove either the top or the bottom 6", the next tie is 12"+ away.
Any thoughts or ideas on how to circumnavigate this criterion and properly trim down this precast column 6"?
Thanks in advance!
MindofBarca