Since we have several members active recently from the prefab wood truss industry I wanted to take a second to ask a question concerning the typical truss output.
For background - When specifying dead load to be used to resist wind uplift, I generally specify 0.6x an approximate of "actual" roof dead in my general notes. This generally equates to around 0.6 x 15 = 9 psf. So even for jobs where I am specifying 20 psf Dead Load (10 PSF @ top chord and 10 psf @ bottom chord), I generally specify for truss suppliers to use 8 psf dead load (DL) resistance for wind uplift calculations (5 PSF @ top chord and 3 psf @ bottom chord). For discussion purposes lets assume all of these loads are service-level ASD loading.
Even though I specify 8 psf DL resistance, we almost always see trusses come back with around 12 psf DL resistance.
Questions:
1. As far as truss output, when truss output shows 12 psf resistance (as shown below), is this already taking account the 0.6, or are the top and bottom chord DL given in the notes further reduced by 0.6 within the truss calculations? (See below for typical note.)
2. Assuming that the 0.6 is already taken into account in these loads provided and this is intended to be 0.6 x 20 = 12 psf, are others allowing this? I have to mark this up on practically every single truss shop I review, and even though I have asked for clarification, I have never been given a satisfactory answer to what exactly the numbers provided in the output represent. Is 12 psf DL for uplift calcs common?
I always run my own loads for truss ties @ bearing, but I would think this would have a significant effect on bottom chord design and required bracing.
For background - When specifying dead load to be used to resist wind uplift, I generally specify 0.6x an approximate of "actual" roof dead in my general notes. This generally equates to around 0.6 x 15 = 9 psf. So even for jobs where I am specifying 20 psf Dead Load (10 PSF @ top chord and 10 psf @ bottom chord), I generally specify for truss suppliers to use 8 psf dead load (DL) resistance for wind uplift calculations (5 PSF @ top chord and 3 psf @ bottom chord). For discussion purposes lets assume all of these loads are service-level ASD loading.
Even though I specify 8 psf DL resistance, we almost always see trusses come back with around 12 psf DL resistance.
Questions:
1. As far as truss output, when truss output shows 12 psf resistance (as shown below), is this already taking account the 0.6, or are the top and bottom chord DL given in the notes further reduced by 0.6 within the truss calculations? (See below for typical note.)
2. Assuming that the 0.6 is already taken into account in these loads provided and this is intended to be 0.6 x 20 = 12 psf, are others allowing this? I have to mark this up on practically every single truss shop I review, and even though I have asked for clarification, I have never been given a satisfactory answer to what exactly the numbers provided in the output represent. Is 12 psf DL for uplift calcs common?
I always run my own loads for truss ties @ bearing, but I would think this would have a significant effect on bottom chord design and required bracing.