Does anybody know how to determine if PRV(PSV) will end with chattering if the orifice is oversized?
 
Replies continue below

Recommended for you

Chattering is caused by excessive (greater than 3% of set pressure and no adjustment in blowdown) inlet pressure drop. It is a relatively high frequency dynamic process.

Cycling is caused by too large an orifice a nozzle size PSV. It is a relatively low frequency dynamic process.