COOLRUNNINGS
Student
- Aug 10, 2023
- 1
Hi Gents, only if you have time can I get your quick opinion on this question? No problem if you are busy.
To make it simple lets say there is a single hose about 25 feet long. Each end of the hose contains a pair of quick connect fittings. (Four quick connect fittings total). Assume a Nipple, Tee and a Pressure Gauge is attached to the free ends. Assume a supply or return line is attached to the free end of the Tees. There is no trapped air in the system.
Then imagine water is flowing through the entire system at 15 GPM and the Delta of the two pressure guages is 19 psig.
Then lets assume I disconnect the two pairs of quick connect fittings and connect the supply directly to the return. This will bypass the original hose and two of the quick connect fittings.
Then assume I adjust a manual valve to set the flow to 15 GPM and I measure the delta of the two gauges to be a pressure drop of 9 psig.
If I am only interested in the pressure drop of the original 25 foot hose and two of the quick connect fittings is it fair to say this region has a pressure drop of (19psig minus 9psig) = 10psig?
In your opinion is this person correct or is he being a jackass? Thanks for the input.
To make it simple lets say there is a single hose about 25 feet long. Each end of the hose contains a pair of quick connect fittings. (Four quick connect fittings total). Assume a Nipple, Tee and a Pressure Gauge is attached to the free ends. Assume a supply or return line is attached to the free end of the Tees. There is no trapped air in the system.
Then imagine water is flowing through the entire system at 15 GPM and the Delta of the two pressure guages is 19 psig.
Then lets assume I disconnect the two pairs of quick connect fittings and connect the supply directly to the return. This will bypass the original hose and two of the quick connect fittings.
Then assume I adjust a manual valve to set the flow to 15 GPM and I measure the delta of the two gauges to be a pressure drop of 9 psig.
If I am only interested in the pressure drop of the original 25 foot hose and two of the quick connect fittings is it fair to say this region has a pressure drop of (19psig minus 9psig) = 10psig?
In your opinion is this person correct or is he being a jackass? Thanks for the input.