I my question is regarding sizing of a blower for an air flow application. The system is as shown in the attached.
My question is regarding my method of calculation. There is a 3way 3" valve in the system and the Air enters the branch portion and must either be directed left of right. Cv value = 130 for branch. The current blower is 366 SCFM @ 6" in H2O and the question is can this be reused. My method is as follows:
1. Converted Cv to K using h = K v^2/2g, The h = 2.3' (1 psi of drop at listed Cv value). v = 5.9 ft/s (which is the velocity of 155 gpm flow in 3" cross section). K value for valve = 4.25
2. Figured K values for 2-4" 90s and 2-4" 45s. Summed K's to get Ktot = 5.85
3. Used Darcy-Weisbach to figure Pdrop at 366 SCFM.
And the value I derived is 9.7" H2O and my conclusion is that this blower may not be reused.
I was a bit skeptical of the Cv conversion to K because specific correlations exist for gas flow systems for figuring pressure drop given Cv. But, a colleague has informed me that this is his preferred method and he has done numerous landfill gas Pdrop calcs with good comparison of calculated results to reality.
Your input is appreciated - thanks!
Rob
I my question is regarding sizing of a blower for an air flow application. The system is as shown in the attached.
My question is regarding my method of calculation. There is a 3way 3" valve in the system and the Air enters the branch portion and must either be directed left of right. Cv value = 130 for branch. The current blower is 366 SCFM @ 6" in H2O and the question is can this be reused. My method is as follows:
1. Converted Cv to K using h = K v^2/2g, The h = 2.3' (1 psi of drop at listed Cv value). v = 5.9 ft/s (which is the velocity of 155 gpm flow in 3" cross section). K value for valve = 4.25
2. Figured K values for 2-4" 90s and 2-4" 45s. Summed K's to get Ktot = 5.85
3. Used Darcy-Weisbach to figure Pdrop at 366 SCFM.
And the value I derived is 9.7" H2O and my conclusion is that this blower may not be reused.
I was a bit skeptical of the Cv conversion to K because specific correlations exist for gas flow systems for figuring pressure drop given Cv. But, a colleague has informed me that this is his preferred method and he has done numerous landfill gas Pdrop calcs with good comparison of calculated results to reality.
Your input is appreciated - thanks!
Rob