Pressure for Class III Stand Pipe - NFPA

Status
Not open for further replies.

Vusal Quliyev

Mechanical
Dec 4, 2018
26
Dear Experts,
there is big confusing at the NFPA 14 to understand.

It is stated that for Class I:
maximum allowed pressure - 175 psi (12.1 bar)
minimum allowed pressure - 100 psi (6.9 bar)

It is stated that for Class II:
maximum allowed pressure - 100 psi (6.9 bar)
minimum allowed pressure - 65 psi (4.5 bar)

My question is about class III system. As you know Class III is combination of Class I and Class II.
So there is no any pressure value to apply class III to comply with class I and class II at the same time. [surprise]
(If I choice 6 Bar it does not complies to Class I. If i choice 8 bar this time it will not complies to class II)
What is your recommendation?

 
Replies continue below

Recommended for you

SprinklerDesigner2, thanks for your Help. Can you refer standard section for this information, please?
 
How does your jurisdiction handle 1 1/2 connections on class III systems? Are you going to install hoses? You will need to study chapter 7 of 14 carefully. See specifically maximum and minimum pressure limitations and everything that deals with 1 1/2 connections.
 
It may be complemented with local or AHJ requirements.
You go with class III and maybe a removable restricting device on 1.5 hose connection or hose valve may solve the class II req.
 