slickstyles5

Aerospace
Jun 23, 2008
111
0
0
CA
Hello,

I read the FM Global Code 7-32, and there is a rule regarding pressure gauges to reduce leakage to a minimum:

"Use restricted orifices in piping connecting the gauges to the equipment."

Would this juste be a needle valve? Or is it referring to some other device?

Thanks

Gabriel
 
Replies continue below

Recommended for you

This would be an orifice plate or some other permanent restriction but not a valve. The idea is that if the gauge fails you have a small hole for the material to escape through. This is common on highly hazardous lines.
 
But if you just slightly crack open a needle valve, wouldn't it work just the same? Are there any standard parts that could be used? It is 1/4" NPT gauges that will be installed. The liquid is jet fuel.
 
A cracked open needle valve will do the job but is not fool proof.
A pressure gauge snubber as suggested by Stonecold.that screwed into the connection will do the job.Snubber are commonly used for dampening out fluctuating pressure.Available off the shell.
 