greenen
Mechanical
- Jul 16, 2015
- 9
Hello all, first time poster here. I have a HVAC pressure loss problem and I am stuck. Here is the background info. I am working on an HVAC renovation project for a commercial office and we are redoing a portion of the return duct work. I am calculating the pressure drop in the return line to confirm that our new air handling unit will not be starved for air and to see if any of the portions of the duct work need to be redone.
The contractor fortunately used lots of rigid duct and has several symmetrical wye fittings, ASHRAE fitting ED5-9. The fitting has two 8" lines coming together with a separation of 60 degrees and they converge into another 8" line. Each inlet line has 180 cfm giving a combined cfm of 360.
Here is my issue, I am trying to find the total pressure loss through this fitting. In the ASHRAE tables for the this fitting with this airflow and geometry my local loss coefficient or "C" value is a negative. This means that the air stream actually gains energy after passing through the fitting. In the ASHRAE Fundamentals it explains that this can happen when one air stream is moving faster than the other. The faster air stream imparts energy to the slower air stream making the slower stream gain energy. My problem is that my two incoming air streams are the same velocity, same cfm, same duct diameter. Yet the tables say that each flow stream has the same negative C value thus each flow stream gains energy. This does not seem right.
What I think is happening is I have 2 8" lines reducing to 1 8" line, the fitting is acting as a nozzle speeding up the airflow. Thus my velocity pressure through the fitting goes up for both air streams, hence the negative C value. But, as a result my static pressure must go down and total pressure must go down. How do I find that drop in total pressure?
Thank you for any help.
The contractor fortunately used lots of rigid duct and has several symmetrical wye fittings, ASHRAE fitting ED5-9. The fitting has two 8" lines coming together with a separation of 60 degrees and they converge into another 8" line. Each inlet line has 180 cfm giving a combined cfm of 360.
Here is my issue, I am trying to find the total pressure loss through this fitting. In the ASHRAE tables for the this fitting with this airflow and geometry my local loss coefficient or "C" value is a negative. This means that the air stream actually gains energy after passing through the fitting. In the ASHRAE Fundamentals it explains that this can happen when one air stream is moving faster than the other. The faster air stream imparts energy to the slower air stream making the slower stream gain energy. My problem is that my two incoming air streams are the same velocity, same cfm, same duct diameter. Yet the tables say that each flow stream has the same negative C value thus each flow stream gains energy. This does not seem right.
What I think is happening is I have 2 8" lines reducing to 1 8" line, the fitting is acting as a nozzle speeding up the airflow. Thus my velocity pressure through the fitting goes up for both air streams, hence the negative C value. But, as a result my static pressure must go down and total pressure must go down. How do I find that drop in total pressure?
Thank you for any help.