Pressure Losses in Air Duct
slickstyles5
Aerospace
Jun 23, 2008
111
I am currently trying to size a Pressure Blower that will be used to cool an engine. A Pipe/Hose of 40 feet will be connected at the outlet of the blower. The flow required is 660 cfm and my hose / pipe size is 5" ID.
Is there a simple way to determine pressure losses (in. H2O) in 90 deg. pipe elbows as well as flexible accordian type hoses?
Please provide some design guides / links that could help.
Thanks!!
i want to see how this pipe elbow looks like in elbow.
there are various types of 90 Deg Elbows in round shape which vary in different manner. Ashrae has a number of fitting database and this can be easily calculated. You can either find ASHRAE Handbook Fundamentals - Duct Design Chapter. or send me a diagram of this elbow. I'll chose the nearest or exact type of elbow & calculate for you by specialized softwares which do this
Hi Walz,
Would you happen to have a pdf document of the types of elbows with the equation to calculate the losses? I would also need an equation for the losses in straight galvanized sections. The elbow will be the most standard one.
Thanks!
Gabriel
i Tried to upload the 7 MB pdf file, but couldnt
and i cant extract the PDF aswell as it is protected.
For straight ducts it very simple, all you need to know is that friction loss rate (in of water / 100ft of duct)
But you need to give me atleast the material of pipe. I will assume it be be flexible metallic and calculate for the duct pressure loss like this.
with 5in as ID and 660 CFM, the friction rate is 15.632 in / 100 ft of duct. Muliply this value by 40/100 to get 6.2528 in of water . thats your result for the duct.
As for as 90 Deg elbow is concerned, i calculate for you at least 5 different types of elbows, and list you their Fitting number, just download the image file for your referrance of these 5 elbow types. Chose the best which suites your elbow kind as i cant chose any of them as standard.
CD3-1 : Pressure Drop = 0.24 in of water
CD3-2 : Pressure Drop = 0.45 in of water
CD3-5 : Pressure Drop = 0.75 in of water
CD3-9 : Pressure Drop = 0.535 in of water
CD3-10 : Pressure Drop = 0.20 in of water
 http://files.engineering.com/getfile.aspx?folder=bdcfb4b2-af9a-42ff-b1b2-61496ab410e2&file=90Deg_Elbows.JPG
Walz,
That's amazing and the values seem very good. I have found my HVAC book and there is some information in there and I will compare to your results to see if they match. Obviously the 7MB file would be great. Would it work by email instead?
Thanks very much for you helps, you're doing the work for me!!
The tough part would be calculating loss through accordion type hose. You might need manufacturer data and percentage hose compression estimates, assuming no sagging. ASHRAE and SMACNA are not real exact on that.
I do have the manufacturer's curves for friction losses due to the hose, so with what I have now I should be ok to size my pressure blower!! Thanks guys!!