MinnesotaSlinger
Mechanical
- Feb 13, 2008
- 23
Hello. I've got a project where I'm going to take steam from 80-100 psig (the header pressure varies somewhat) and deliver it to a shell-and-tube HX. Earlier in the design process, I assumed that I would put in a PRV to reduce pressure to 50 psig, and with the HX I have quoted for the project, it is sized assuming 50 psig. (The design pressure for the unit is 150 psig.) At 50 psig and the values I provided for required heat transfer, water inlet temp, and water flow rate, I have a unit quoted that meets those conditions.
Between the PRV and the HX, I've assumed that I would install a control valve that is controlled by outlet water temperature. By having a PRV and control valve is series, I will have knocked steam pressure down to my design condition of 50 psig and will be able to regulate flow into the HX to maintain my necessary HX. But something about having a PRV and a control valve in series strikes me as sort of dumb and a waste of money. Would I really need a PRV ahead of the control valve? I don't really know that there is any harm in pressure going above my 50 psig design parameter. And assuming that the HX is operating close to design conditions, I would think the one valve would hold back flow such that the pressure in the HX would be about 50 psig, a little more or less depending on, say, how clean the tubes are.
Anyway, if you have a steam header that varies in pressure, should you just get a HX sized and capable of operating at the low end of that range? (I could go back to the vendor and size for 80 psig.) Should you get it sized for a lower pressure and put in a PRV to drop pressure to that level ahead of a separate control valve (and in so doing, you wouldn't be subject to pressure fluctuations in the steam header)? Can you just size a HX based on some pressure lower than the low end of the steam header pressure, skip installing a PRV, and just let a control valve control steam flow?
Words of wisdom about how to ensure proper operation of an F&T steam trap and other condensate concerns related to strict or unrestricted HX pressure control is also appreciated. Thanks.
Between the PRV and the HX, I've assumed that I would install a control valve that is controlled by outlet water temperature. By having a PRV and control valve is series, I will have knocked steam pressure down to my design condition of 50 psig and will be able to regulate flow into the HX to maintain my necessary HX. But something about having a PRV and a control valve in series strikes me as sort of dumb and a waste of money. Would I really need a PRV ahead of the control valve? I don't really know that there is any harm in pressure going above my 50 psig design parameter. And assuming that the HX is operating close to design conditions, I would think the one valve would hold back flow such that the pressure in the HX would be about 50 psig, a little more or less depending on, say, how clean the tubes are.
Anyway, if you have a steam header that varies in pressure, should you just get a HX sized and capable of operating at the low end of that range? (I could go back to the vendor and size for 80 psig.) Should you get it sized for a lower pressure and put in a PRV to drop pressure to that level ahead of a separate control valve (and in so doing, you wouldn't be subject to pressure fluctuations in the steam header)? Can you just size a HX based on some pressure lower than the low end of the steam header pressure, skip installing a PRV, and just let a control valve control steam flow?
Words of wisdom about how to ensure proper operation of an F&T steam trap and other condensate concerns related to strict or unrestricted HX pressure control is also appreciated. Thanks.